Andy,
A few more thoughts on the subject for everybody.
You're happy with this situation for heat conservation - however time may tell a sorry story for the grout and silicones in the room (as well as, possibly, the transducer)particularly in Alastairs place where heating is likely to set back for extended periods and then the lower dew point will leave more free water sitting about for a while
IMO your 'issues' stem from two reasons:
First - the speed of response of the transducer is too quick and is therefore reading 'transducer local' conditions and switching the extract off too soon. the RH then reequilibrates in the room and the system switches in again. This situation repeats until RH equilibrates below threshold - classic underdamped analouge control loop!!
Options - to keep the fast response time you need to apply some integral action to reduce overshoot. The simpler option is to reduce the proportional action. Probably both a s part of a tuning exercise (Andy, remember Zeiger Nichols? and the ridiculously over sensitive adjustments on Kent controllers, bellowes pumping till they popped :-)
Neither easy to do properly in the brick itself, so necesitating external circuitry followed by tuning - a amusing divertion for those of us with too much time:-) to make a living just buy a humidistat where all this work is largely done for you.
Alternatively apply a much larger switching hysteresis to the system ie fan overrun via dwell as Lawrenece suggested earlier.
Analogue instruments interfaced with digital actuators are often problematical in terms of loop stability - the digital action introduces 'high frequency' harmonics into the loop which can destabilise the same way as any high bandwith feedback loop cf the need for low pass debonce filters on the brick DI
Another approach to taming this may be to use a speed controlled fan that ramps down with decreasing humidity. This would give yo several other possible benefits interms of setback speeds at night etc. I think Justin Mackey is doing something along these lines - not sure if he is controlling on humidity though, Justin?
The second issue - the condensing. The sub kennel sized British bathroom is never going to be anything other than a 'condesing environment' without blowing a noisy, energy consuming gale through, while webbrick builds are quite likely to be in larger properties, any gains in siting possibilities are likely to be offset by the probable lowering in effectivness of extract. While keeping the transducer in the airflow is one method of controlling condensation it is at odds with achieving fast acting tight band control.
IMO any encasing/heating/wafting etc is really only reproducing a commercially available stat, at which point one has to ask if the bare transducer is suitable.
In ducted fans/centralised systems one could use an in room transducer for fast switch on and a downstream sensor to switch off - this is just another way of increasing switching hysteresis albeit with greater level of band control than a one size fits all dwell.
The all time best solution I've ever found to humidity in the bath room - open the window:-) ......now what sort of actuator........
I'm gonna stop now as I sense I have probably drifted some way past OT
Cheers
Simon